Didn't find this in a search of the forums. Has anyone dealt with plumbing codes and specifically, the main vent on the drain system? In a typical framed house, the vent goes through the roof but that's not an option for a yurt. The codes are damn specific and not compatible with yurts.

I can think of plenty of ways to accomplish this functionally and my place is remote enough the plumbing inspector may pass anything for want of not coming back, but I'm curious if anyone here has dealt with pluming inspectors and if so, what did they allow or not allow?

I will post whatever I learn but if I can leverage others' experiences first I'd like to.

skihuckster is offline   Reply With Quote
Old 04-24-2022, 07:37 AM   #2
Yurt Forum Member
 
trihartsfield's Avatar
 
Join Date: Jun 2017
Location: Sheridan, MT
Posts: 45
Default Re: Plumbing vent

That is going to depend on your location.

You will probably have to contact your local inspector and get his/her take on this. As an FYI, most who have a yurt, especially if they live in it, have a wood stove. The pipe goes either through the tono or the side. Ours goes through the side and can be sealed enough to be safe. Note sure if that is an option. That is a question you will have to discuss with the inspector.

Chris
trihartsfield is offline   Reply With Quote
Old 04-24-2022, 02:48 PM   #3
Yurt Forum Addict
 
Join Date: Nov 2013
Posts: 2,193
Default Re: Plumbing vent

Not on a yurt. But around here inspectors cut you NO slack at all. The gov't wants no lawsuits against them, believe me. One of my mantles flunk because the top was>> >1/4"<<< too wide per spec book that came with the insert. I sh%$ you not. 1/4". I wanted to kick that dudes a$$ into next week.
Bob Rowlands is offline   Reply With Quote
Old 04-24-2022, 07:09 PM   #4
Yurt Forum Member
 
Join Date: Dec 2021
Posts: 37
Default Re: Plumbing vent

Well that's not promising.

Since my deck is off the ground I was thinking of teeing my vent off the main drain where it will exist under the deck structure and bringing the vent pipe over to the stove pipe and using that support to also support the vent to a proper elevation. Yes I could run it out the wall through a grommet like the stove pipe but I prefer not to.

The inspector has no idea what a yurt is. His inspection will probably be the first time he's seen one.

More than ideas I'm looking for any examples of when folks on this forum did it wrong and didn't pass. If I fail inspection I hope it's on a design that hasn't been tried/flunked before.
skihuckster is offline   Reply With Quote
Old 04-24-2022, 08:46 PM   #5
Yurt Forum Addict
 
Join Date: Nov 2013
Posts: 2,193
Default Re: Plumbing vent

Wish I could give good advice here but I'm no plumber. I do know when I built our house (year 1999 codes applied) there had to be a vent stack directly up and through the attic and roof, within 10 lineal feet of any/all drains. Sink, tub, toilet, shower, clothes washer, dishwasher. If it had a drain, 10' max to stack. Of course there was a stack size minimum diameter as well.

The dude that plumbed my house was a pro plumber friend and he was real upfront about what he had to do to get everything to pass inspection. I didn't get gigged on plumbing. My own work did though. But that's another story.

Last edited by Bob Rowlands; 04-24-2022 at 08:48 PM. Reason: typos as usual
Bob Rowlands is offline   Reply With Quote
Old 12-09-2024, 12:09 AM   #6
Yurt Forum Youngin
 
Join Date: Dec 2024
Posts: 2
Default Re: Plumbing vent

One thing I’ve seen is folks running the vent pipe out through a wall instead of the roof. I know a guy who plumbed his own cabin like that, and the inspector didn’t bat an eye.
Beckeye is offline   Reply With Quote
Old 12-09-2024, 12:34 AM   #7
Yurt Forum Member
 
Join Date: Dec 2021
Posts: 37
Default Re: Plumbing vent

I had forgotten about this post from 2y ago but can update on the final result, which passed a couple months ago. I vented all my sinks with an AAV indoors (behind an access panel on the bathroom wall). All the drains went below the floor and combined into a stand pipe that drains to the septic tank. Off that stand pipe I put a Y fitting and extended a 3" vent sideways (to clear yurt wall) and then up to a point 10' above the floor elevation of the yurt. I supported it the same way many support stove pipes on yurts.

That satisfied the inspector without arm twisting. I had to deal with a pair of them: one wanted the 3" vent, the other thought 1-1/2" was more than enough.
skihuckster is offline   Reply With Quote
Old 12-09-2024, 12:42 PM   #8
Yurt Forum Addict
 
Join Date: Nov 2013
Posts: 2,193
Default Re: Plumbing vent

IMO the inspector signed off on your 'custom' vent because it was a one off install that was gonna work fine regardless of the code spec.

Residential subdivision around here they wouldn't have. I got gigged on 10 items. Some were BS. And some weren't. I'm especially glad the inspector caught a basement 'form step' violation of 6' drop where 4' was maximum. The day before the pour.

Plus I caught another foundation form mistake myself where the foundation morons missed a counterfort clearly marked on the plan. That would REALLY have screwed up my front deck and roof foundation at the front of the house. It would have cost >thousands< to correct. Effing illegal morons led by a foreman that couldn't have cared less about the accuracy of his work. I had an entire set of trusses rebuilt over the laundry from that dumbass building the footer 8" on the wrong side of a foundation line.

Of course the items I got gigged on in my carpentry work were total BS. lol
Jafo likes this.

Last edited by Bob Rowlands; 12-09-2024 at 12:48 PM.
Bob Rowlands is offline   Reply With Quote
Old 12-11-2024, 02:20 AM   #9
Yurt Forum Youngin
 
Join Date: Dec 2024
Posts: 2
Default Re: Plumbing vent

Quote:
Originally Posted by Beckeye View Post
One thing I’ve seen is folks running the vent pipe out through a wall instead of the roof. I know a guy who plumbed his own cabin like that, and the inspector didn’t bat an eye.
If you’re stuck, it might be worth having a pro take a look. I’ve had to call in help when I hit a wall (pun intended) on stuff like this.

Last edited by Jafo; 12-12-2024 at 04:58 PM.
Beckeye is offline   Reply With Quote
Old 12-11-2024, 12:34 PM   #10
Yurt Forum Addict
 
Join Date: Nov 2013
Posts: 2,193
Default Re: Plumbing vent

You're fortunate to have a cool plumbing crew that speaks English and understands what you want them to do.

Why would I sat that? Nowadays around here, you'll quite possibly be talking with a foreman that's bilingual. What you actually want done can get lost in translation, or dropped simply because because the crew is gonna roll the way they want. What you want is unimportant. "We doan need no stinkin badges!" lol

The crew does what the foreman tells them. He may not be telling them what you want because he knows you don't speak their language. You can be standing there talking what you want with the foreman and watching the crew doing something else. I've had that happen. Nowadays in construction, bilingualism is a real problem.
Bob Rowlands is offline   Reply With Quote
Reply

Tags
None


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



All times are GMT -5. The time now is 10:22 AM.


Yurt Forum | Buying a Yurt | Building a Yurt | Yurt Life | Yurts for Sale | Yurt Glamping | Yurts Pricing Yurt Calculators | Yurt Insurance | Yurt Insulation | Yurt Classifieds

Copyright 2012 - 2024 Jeff Capron Inc.

Yurt Posts Delivered to your Email!

Stay up-to-date with all the new yurt posts to your inbox!

unsusbcribe at anytime with one click

Close [X]